• Welcome to New Brunswick Craft Brewers Association.

Electrical Power Cord Type

Started by Jake, September 10, 2014, 08:22:39 PM

Previous topic - Next topic

0 Members and 3 Guests are viewing this topic.

brew

Not grounding your equipment properly is just a bad idea - no offense James but using the ground wire in a 3 wire cable as a neutral line, and not grounding anything to the panel is not only illegal, it can be dangerous (not saying I've never done that though!). Going 4 wire gives you the ability to have a proper neutral wire giving both 240 and 120, while at the same time allowing you to ground your equipment to the panel (where its supposed to). I have a few fireman friends who have told me about electrical fires caused by improper or absent grounding. I hadn't realized how bad it can be, especially around liquids. I'm guessing that's why its been in the electrical code for such a long time.

In a new house with new everything to go with it, getting 3 wire is just creating a problem that needs to be solved. Just solve it now and get 4 wire. While you're at it, get nice heavy stuff as well - 8 gauge will give you lots of room to have nice big ass circuits. You'll never have to think about it again...
NBCBA Treasurer
Planned: Drink beer later, Primary: Drink beer soon, Secondary: Drink beer shortly, Kegged: Drinking beer now

JohnQ

A little off topic, but kind of the same,
Just bought one of these for our delivery vehicle, going to be delivered next week...

http://www.mitsubishi-motors.ca/en/vehicles/i-miev/2014/trims/es/

We'll be discussing electrical cords too!

JQ
Charter Member
I'm on the 12 step program...
I'm on Step 1 - I've admitted I have a problem...and if you're reading this, so do you!

On Tap: 1. MT; 2. PartiGyle Barley Wine; 3. MT; 4. MT; 5. Obiwan Kanobe 6. Pollen Angels TM Base; 7. MT  8. MT
Visiting Taps:
Travelling: Vienna Pale @ RB's; NB55 @ Fakr's
Recent Visitors: CMC Graham Cracker Brown, Fakr's Warrior AGDTDiPA; Brew's SNPA; Brew's C^3, Fakr's Stout
In the BH's: 1. Empty 2. WW, STILL! 3. Empty
Aging: Lots and Lots of Mead for Samples

JamesC

Quote from: brew on September 12, 2014, 10:40:31 AM
Not grounding your equipment properly is just a bad idea - no offense James but using the ground wire in a 3 wire cable as a neutral line, and not grounding anything to the panel is not only illegal, it can be dangerous (not saying I've never done that though!). Going 4 wire gives you the ability to have a proper neutral wire giving both 240 and 120, while at the same time allowing you to ground your equipment to the panel (where its supposed to). I have a few fireman friends who have told me about electrical fires caused by improper or absent grounding. I hadn't realized how bad it can be, especially around liquids. I'm guessing that's why its been in the electrical code for such a long time.

In a new house with new everything to go with it, getting 3 wire is just creating a problem that needs to be solved. Just solve it now and get 4 wire. While you're at it, get nice heavy stuff as well - 8 gauge will give you lots of room to have nice big ass circuits. You'll never have to think about it again...

I never said to not ground your equipment, or the panel for the record. I would just do it slightly differently. I also wouldn't do that on a permanent install. If you're hard wiring something to your main panel, that's where the CEC comes in for sure.

pliny


Jake

Screw it I'll stick with propane  :facepalm:
President of the NBCBA

Two Wheeler

Quote from: Jake on September 12, 2014, 12:47:43 PM
Screw it I'll stick with propane  :facepalm:

I just took a few steps back from my e-brewery desires, haha  :frazzled:
Jordan Harris
BIAB'er

Roger

Electric brewing is not nearly as difficult as it may seem. Once your set up its like magic.  :banana: